Salon and Barbershop Title 24 Requirements
Part 6 names barbershops, beauty salons and nail salons in its ventilation tables, so a salon is one of the clearest occupancy-specific cases. Outdoor air is 0.4 cfm per square foot, exhaust is 0.60 for beauty and nail salons and 0.50 for barbershops, and demand control ventilation may not be used.
- Send your plans
- Get a free quote
- Approve it
- Report in 4–5 business days
A 1,200 square foot salon, worked through
- Outdoor air: the table density of 17 people per 1,000 square feet gives 20.4 people at 15 cfm, or 306 cfm. Equation 120.1-F takes the larger of that and the area term, 0.4 times 1,200, so 480 cfm governs.
- Exhaust: 0.60 cfm per square foot is 720 cfm for a beauty or nail salon, and 0.50 is 600 cfm for a barbershop.
- Lighting: the barber, beauty salon and spa category allows 0.70 watts per square foot, 840 watts here.
Where nail salons sit
There is no separate nail row. Beauty and nail salons share one row in Table 120.1-A and one in Table 120.1-B, both Class 2 air. A treatment room that matches neither takes the class of the most similar listed space under Section 120.1(g)7.
No CO2 sensors
Exception 2 to Section 120.1(d)3 bars demand control ventilation in barbershops, beauty salons and nail salons. The 17 per 1,000 default sits below the 25 trigger anyway, but the bar holds even if the egress load factor is higher.
What a salon fit-out actually triggers
Part 6 attaches these rates to ventilation equipment that is new or altered (Section 141.0(b)2). If moving into a former shop changes the occupancy classification, Section 141.0(b) applies to the salon occupancy rather than the shop (Note 1 to Section 141.0). The lighting category adds 0.30 watts per square foot for detailed task work or 0.25 for decorative and display lighting, but only if the plans show the task areas, the task takes at least two hours a day, and the luminaires are separate from general lighting. File NRCC-MCH-E for the air system and NRCC-LTI-E for the lights.
See salons and spas, commercial ventilation, change of use and lighting power allowances. Our commercial service quotes salon projects.
Common Title 24 Questions
- When does a commercial project need Title 24?
- Does an office tenant improvement need Title 24?
- Does a restaurant remodel need Title 24?
- Does a retail tenant improvement need Title 24?
- What plans are needed for a commercial Title 24 report?
- What is an NRCC certificate of compliance?
Frequently Asked Questions
They share the beauty salon row at 0.60 cfm per square foot of exhaust and 0.4 cfm per square foot of outdoor air, both Class 2 air.
No. Exception 2 to Section 120.1(d)3 names barbershops, beauty salons and nail salons among the spaces that may not install it.
Explore Building Types
- Title 24 Requirements for Auto Repair Shops
- Title 24 Requirements for Banks and Financial Institutions
- Title 24 Requirements for Cannabis Cultivation Facilities
- Title 24 Requirements for Car Dealerships
- Title 24 Requirements for Churches and Assembly Buildings
View all Building Types guides → · Commercial Title 24 · Title 24 guide